Power in Alternating-Current Circuits — Question 4

Section 31-9 · Physics pages 5138–5139

Question 4 Partial power-factor correction requires the difference of reactive powers A load has real power P and initial lagging power factor p1. It is supplied at fixed rms voltage V and angular frequency omega. A parallel capacitor is to improve source power factor to lagging p2 > p1. ∼ V load C Schematic; labels, not drawing lengths, specify the data. (a) Derive the capacitance in terms of both phase angles. (b) For p1 = .600 and p2 = .900, find the fraction of the unity-correction capacitance required.
Show solutionHide solution
Question 4 - Solution Partial power-factor correction requires the difference of reactive powers ∼ V load C (a) Method and calculation ϕ1 = cos−1 p1, ϕ2 = cos−1 p2, Qbefore = P tan ϕ1. C = P(tan ϕ1 −tan ϕ2) ωV 2 . (b) Interpretation and further calculation Cunity = P tan ϕ1/(ωV 2). C/Cunity = 1 −tan(cos−1 .900) tan(cos−1 .600) = .636758 . Physical check Subtract reactive powers, not power factors; the latter are nonlinear functions of phase.

Question 4

Partial power-factor correction requires the difference of reactive powers

A load has real power P and initial lagging power factor p1p_1. It is supplied at fixed rms voltage V and angular frequency omega. A parallel capacitor is to improve source power factor to lagging p2>p1p_2>p_1.

Diagram shown in the original SVG worksheet.

  1. Derive the capacitance in terms of both phase angles.

  2. For p1=.600p_1=.600 and p2=.900p_2=.900, find the fraction of the unity-correction capacitance required.

Question 4 - Solution

Partial power-factor correction requires the difference of reactive powers

Diagram shown in the original SVG worksheet.

(a) Method and calculation

ϕ1=cos⁡−1p1,ϕ2=cos⁡−1p2,Qbefore=Ptan⁡ϕ1.\phi_1=\cos^{-1}p_1,\quad\phi_2=\cos^{-1}p_2,\quad Q_{\mathrm{before}}=P\tan\phi_1.C=P(tan⁡ϕ1−tan⁡ϕ2)ωV2.\boxed{C=\frac{P(\tan\phi_1-\tan\phi_2)}{\omega V^2}}.

(b) Interpretation and further calculation

Cunity=Ptan⁡ϕ1/(ωV2).C_{\mathrm{unity}}=P\tan\phi_1/(\omega V^2).C/Cunity=1−tan⁡(cos⁡−1.900)tan⁡(cos⁡−1.600)=.636758.\boxed{C/C_{\mathrm{unity}}=1-\frac{\tan(\cos^{-1}.900)}{\tan(\cos^{-1}.600)}=.636758}.

Physical check

Subtract reactive powers, not power factors; the latter are nonlinear functions of phase.