Question 9 A sine-calibrated average meter misreads a square wave A meter measures mean absolute voltage and multiplies it by a calibration constant so it reports the correct rms for any sine wave. It is then connected to a symmetric square wave with amplitude A. ωt v Schematic; labels, not drawing lengths, specify the data. (a) Derive the calibration constant. (b) Find the displayed reading and percentage error relative to the true square-wave rms.
Show solutionHide solution
Question 9 - Solution A sine-calibrated average meter misreads a square wave ωt v (a) Method and calculation ⟨|vsine|⟩= 2Vp/π, Vsine,rms = Vp/ √ 2. k = π/(2 √ 2) = 1.11072 . (b) Interpretation and further calculation ⟨|vsquare|⟩= A = Vsquare,rms. Vdisplay = 1.11072A, error = +11.0721% . Physical check A true-rms instrument and a sine-calibrated averaging instrument need not agree for nonsinusoidal signals.

Question 9

A sine-calibrated average meter misreads a square wave

A meter measures mean absolute voltage and multiplies it by a calibration constant so it reports the correct rms for any sine wave. It is then connected to a symmetric square wave with amplitude A.

Diagram shown in the original SVG worksheet.

  1. Derive the calibration constant.

  2. Find the displayed reading and percentage error relative to the true square-wave rms.

Question 9 - Solution

A sine-calibrated average meter misreads a square wave

Diagram shown in the original SVG worksheet.

(a) Method and calculation

⟨|vsine|⟩=2Vp/π,Vsine,rms=Vp/2.\langle|v_{\mathrm{sine}}|\rangle=2V_p/\pi,\quad V_{{\mathrm{sine}},\mathrm{rms}}=V_p/\sqrt2.k=π/(22)=1.11072.\boxed{k=\pi/(2\sqrt2)=1.11072}.

(b) Interpretation and further calculation

⟨|vsquare|⟩=A=Vsquare,rms.\langle|v_{\mathrm{square}}|\rangle=A=V_{{\mathrm{square}},\mathrm{rms}}.Vdisplay=1.11072A,error=+11.0721%.\boxed{V_{\mathrm{display}}=1.11072A,\quad\text{error}=+11.0721\%}.

Physical check

A true-rms instrument and a sine-calibrated averaging instrument need not agree for nonsinusoidal signals.