Entropy in the Real World: Refrigerators — Question 2

Section 20-5 · Physics pages 3314–3315

Question 2 Entropy generation raises the work required for a fixed cooling load For a cyclic refrigerator, Qh = Qc + W, where Qc is heat removed from the cold region and W is work input. Define KR = Qc/W and heating coefficient KH = Qh/W. A refrigerator removes 1350 J per cycle from 270 K and rejects heat to 300 K. Th refrigerator Tc Qc Qh W Heat and work labels denote positive magnitudes in the arrow directions. (a) Derive the minimum work and maximum KR using the reservoir entropy balance. (b) If actual work is 225 J, find actual KR, rejected heat and entropy generation.
Show solutionHide solution
Question 2 - Solution Entropy generation raises the work required for a fixed cooling load Th refrigerator Tc Qc Qh W (a) Method and calculation Sgen = Qc + W Th −Qc Tc ≥0 ⇒W ≥Qc (Th Tc −1 ) . Wmin = 1350(300/270 −1) = 150 J, KR,max = 270 300 −270 = 9.00. (b) Interpretation and further calculation KR = 1350/225 = 6.00, Qh = 1575 J. Sgen = 1575/300 −1350/270 = .250 J/K. W −Wmin = 75 J = ThSgen. The extra work ultimately increases heat rejection to the warm reservoir. Physical check The cold load is held fixed in the work comparison.

Question 2

Entropy generation raises the work required for a fixed cooling load

For a cyclic refrigerator, Qh=Qc+WQ_h=Q_c+W, where QcQ_c is heat removed from the cold region and WW is work input. Define KR=Qc/WK_R=Q_c/W and heating coefficient KH=Qh/WK_H=Q_h/W. A refrigerator removes 1350 J per cycle from 270 K and rejects heat to 300 K.

Diagram shown in the original SVG worksheet.

  1. Derive the minimum work and maximum KRK_R using the reservoir entropy balance.

  2. If actual work is 225 J, find actual KRK_R, rejected heat and entropy generation.

Question 2 - Solution

Entropy generation raises the work required for a fixed cooling load

Diagram shown in the original SVG worksheet.

(a) Method and calculation

Sgen=Qc+WTh−QcTc≥0⇒W≥Qc(ThTc−1).S_{\mathrm{gen}}=\frac{Q_c+W}{T_h}-\frac{Q_c}{T_c}\ge0\ \Rightarrow\ W\ge Q_c\left(\frac{T_h}{T_c}-1\right).Wmin=1350(300/270−1)=150J,KR,max=270300−270=9.00.W_{\min}=1350(300/270-1)=150\,\mathrm J,\quad K_{R,\max}=\frac{270}{300-270}=9.00.

(b) Interpretation and further calculation

KR=1350/225=6.00,Qh=1575J.K_R=1350/225=6.00,\quad Q_h=1575\,\mathrm J.Sgen=1575/300−1350/270=.250J/K.S_{\mathrm{gen}}=1575/300-1350/270=.250\,\mathrm{J/K}.W−Wmin=75J=ThSgen.W-W_{\min}=75\,\mathrm J=T_hS_{\mathrm{gen}}.The extra work ultimately increases heat rejection to the warm reservoir.

Physical check

The cold load is held fixed in the work comparison.